High Voltage Engineering
EE 751
Question 95
Question
2082 ShrawanChapter 4: Insulation Coordination4.3 Insulation Protection Level for Temporary, Switching and Lightning Over Voltages
A 132 kV line is terminated by transformer and is protected by an arrester of rating 120 kV located at the incoming line. The BIL withstand voltage of the transformer is chosen to be 500 kV. The protective ratio of transformer is 1.2. Check whether the transformer is properly coordinated with the arrester if a lightning strike of 8,000 kV incident at the arrester.
| Discharge Current | Residual Voltage |
|---|---|
| 10 kA | 300 kV |
| 20 kA | 360 kV |